Currently designing a pier foundation for a PEMB building, and am trying to wrap my head around best practices for shear transfer between the anchor bolts and the pier. The column I'm looking at has 97k (ult) of compression alongside its worst case shear of 37 k (ult). After looking through a bunch of threads on this topic I'd like some opinions on a few questions I have:
- Shear breakout is controlling for any reasonable pier size, leading me towards shear breakout reinforcement per Widianto. Is there any advantage I can take for the heavy compressive load I have on this column alongside the reinforcement. Intuitively it feels like I should get some benefit.
- Widianto outlines the 20ksi limit for nodes at seismic hooks, which is quite limiting. I'd like to take advantage of the typical ties alongside additional stirrups, and I don't overly trust schemes that call for alternating ties to actually be built that way. This previous eng-tips thread mentions a study that the hook alone (not wrapped around a transverse bar) is enough to fully develop the bar. It seems that the 20ksi is very limiting, and maybe this just points to specifying stirrups darn near anytime you need shear breakout reinforcement. Curious to hear what others typically do.
- In normal building design I'm well aware of the issue of shear transfer through anchor rods alone, and that only 2 bolts can be relied on due to the oversize baseplate holes without welding washers to the plate. On PEMB buildings, I've yet to meet an engineer who specifies weld washers to the baseplates, saying it's on the PEMB designer to get the load into the anchor bolts. I also have yet to see any welded washers once the building is erected, but with quick numbers you clearly need more than just two of the anchor bolts for shear transfer. Am I missing something?