how do you calculate the per unit impedance value of a transformer given the percentage impedance value? How do you also estimate the per unit vales of resistance and reactance from the percentage impedance value?
 
Replies continue below

Recommended for you

Per Unit is same thing as percentage. Only a factor 100 different.

So, if you have 5.6 % that will be equal to 0.056 p.u.

The impedance of a power transformer (10+ kVA) is almost purely reactive. You can safely assume close to 90 degrees impedance. If you need better values, you have to ask the manufacturer for data,

Gunnar Englund
 
I think skogsgurra must have meant (10+ MVA). Distribution transformers have X/R ratios ranging from 1 to 6.

You can calculate %R from the load (copper) losses divided by the rating times 100. %X is sqrt(%Z²-%R²).
 
Thanks, jghrist. But I actually meant kVA. It all depends on what you mean with "almost purely reactive" - a matter of discussion. Someone?

Gunnar Englund
 
Also if you know actual R in ohms from copper losses, to get the p.u. value, you need to divide it by the base Z which is base ( rated) L-N voltage divided by the base current. The base current is the rated current.
 
Just to summarize,

%impedance means, the ratio of impedance voltage drop at full load to the normal voltage, when multiplied by 100.

Let us take LV side of the trafo as base values,

%Z= I Z ÷ V, where Z is actual impedance or leakage impedance referred to LV side, and V & I are rated values of LV side.

then,

Z = %Z V ÷ I --- referred to LV side of trafo

%R = Full Load Cu losses ÷ trafo rating in VA ,
(R = Full Load Cu losses /I*I - ref to LV)

%X = sqrt {%Z*%Z - %R*%R}


P.U. impedance = % impednace / 100
or
actual impedance / base impedance.

Where, base impedance = V / I (rated values of base side i.e LV side )

or

KV* KV*1000 / KVA, ( where KV is LV side voltage).

hope this help you.

Varri
 
See the enclose figure to determine approx. the X/R Ratio

X~Z ==> R~Z/(X/R)


XFMR_XoverR.jpg
 