corvalan
Electrical
- Jan 14, 2008
- 17
I was asked the following simple question that made me evaluate what I always thought a as a given.
When the NEC suggests in the informational notes to keep feeders and branches percent voltage drop below 3% and bus percent voltage drop below 5% is it with respect to the NOMINAL voltage of the system (I.e. 480 V) or to the voltage at the secondary terminals of the transformer feeding the system?
The difference of percentage voltage drop considering the NOMINAL voltage or the transformer secondary terminal voltage as the reference starting voltage could be substantial.
Let's assume a transformer has a nameplate voltage rating of 13,200 V to 480 V and is connected at the primary to a system that has an ACTUAL voltage identical to the NOMINAL voltage of 13,200 V.
Due to INTERNAL impedance of the transformer, the transformer secondary terminals will experience a voltage drop from the NOMINAL secondary voltage.
If we calculate PERCENT voltage drop downstream, the results are going to be less than if we calculate PERCENTAGE voltage drop based on the transformer secondary nominal voltage.
The question is:
Is there a standard that explicitly recommends calculating PERCENT voltage drop using the NOMINAL voltage as a base or the diminished transformer secondary voltage as a base?
When the NEC suggests in the informational notes to keep feeders and branches percent voltage drop below 3% and bus percent voltage drop below 5% is it with respect to the NOMINAL voltage of the system (I.e. 480 V) or to the voltage at the secondary terminals of the transformer feeding the system?
The difference of percentage voltage drop considering the NOMINAL voltage or the transformer secondary terminal voltage as the reference starting voltage could be substantial.
Let's assume a transformer has a nameplate voltage rating of 13,200 V to 480 V and is connected at the primary to a system that has an ACTUAL voltage identical to the NOMINAL voltage of 13,200 V.
Due to INTERNAL impedance of the transformer, the transformer secondary terminals will experience a voltage drop from the NOMINAL secondary voltage.
If we calculate PERCENT voltage drop downstream, the results are going to be less than if we calculate PERCENTAGE voltage drop based on the transformer secondary nominal voltage.
The question is:
Is there a standard that explicitly recommends calculating PERCENT voltage drop using the NOMINAL voltage as a base or the diminished transformer secondary voltage as a base?