Hi all,
We have a lot of PFC equipment on site, but one of them, despite working away does not show any current use on its supply meter.
This is a 1MVA Schneider Electric PFC with capacitors and inductors internal. It is fed through a Masterpact MTZ2 breaker at 400V. Neither the separate power meter or the Micrologic controller on the masterpact show any current flowing. I have put our Fluke PQA on the outgoing tails and it also doesn't show any current use.
The meters on the two sections on the PFC were showing 400ish amps on each side, so 800A, but still nothing showing on the supply side.
Can anybody tell me why? It's doing my head in.
We have a lot of PFC equipment on site, but one of them, despite working away does not show any current use on its supply meter.
This is a 1MVA Schneider Electric PFC with capacitors and inductors internal. It is fed through a Masterpact MTZ2 breaker at 400V. Neither the separate power meter or the Micrologic controller on the masterpact show any current flowing. I have put our Fluke PQA on the outgoing tails and it also doesn't show any current use.