Okay.....I am troubleshooting a plant that processes "dirty" water in a reverse osmosis plant and they have had issues regarding pH control of the permeate which is discharged to the environment.
Caustic is added before and after the water passes through the R.O. membranes to bring up the pH. Each line has a dedicated PD metering pump that doses in caustic based on the feedback from the pH probe on the permeate.
I have only toured the plant today and these are some things that I noticed that could be contributing to the instability of the pH control. Please give feedback!!
1. There is essentially the "old side" of the plant and the "new side" of the plant and they are mirror images of each other. The pH of the R.O. permeate is measured in a common sump which both sides of the plant connect to. I see this as a problem as this pH reading is supposed to control both sides of the plant.There is a static mixer after caustic is injected to each side of the plant and there is sample ports downstream of the static mixer but no pH probes?
2. The caustic is a 50% solution and they have had gelling issues. Tank is heated and all lines are heat traced. Could dilution help?
3. The pumps dose a small amount of caustic every 2 or 3 seconds. There is a long distance between the pumps and the injection points (upwards of 160 ft is the longest). There is no check valve at the injection point, is it possible that water is backflowing into the injection line? If so would this affect the caustic addition?
4. I am going to try and let the operator let me perform a step test tomorrow morning to see what the time delay of the pH control loop is.
Any comments or suggestions are welcome!! Sorry for the long winded background
Nathan
Caustic is added before and after the water passes through the R.O. membranes to bring up the pH. Each line has a dedicated PD metering pump that doses in caustic based on the feedback from the pH probe on the permeate.
I have only toured the plant today and these are some things that I noticed that could be contributing to the instability of the pH control. Please give feedback!!
1. There is essentially the "old side" of the plant and the "new side" of the plant and they are mirror images of each other. The pH of the R.O. permeate is measured in a common sump which both sides of the plant connect to. I see this as a problem as this pH reading is supposed to control both sides of the plant.There is a static mixer after caustic is injected to each side of the plant and there is sample ports downstream of the static mixer but no pH probes?
2. The caustic is a 50% solution and they have had gelling issues. Tank is heated and all lines are heat traced. Could dilution help?
3. The pumps dose a small amount of caustic every 2 or 3 seconds. There is a long distance between the pumps and the injection points (upwards of 160 ft is the longest). There is no check valve at the injection point, is it possible that water is backflowing into the injection line? If so would this affect the caustic addition?
4. I am going to try and let the operator let me perform a step test tomorrow morning to see what the time delay of the pH control loop is.
Any comments or suggestions are welcome!! Sorry for the long winded background
Nathan