Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations GregLocock on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

phase difference on single phase residential services. 1

Status
Not open for further replies.

bgisborn

Electrical
Dec 17, 2004
4
I've noticed that most texts show a 180 phase difference on the the two legs derived from a wye-delta 3 phase transformer when this is used for residential service. Forgive me, but I have a real lapse here. The 3 phases are 120 degrees out of phase with each other. Therefore it seems such a 3 phase derived 3 wire single phase service (assume grounded conductor is centrally tapped on one of the phases)should be 120 degrees out of phase with each other-not 180 degrees, which would give the fully balanced neutral current a value of 0. I know I'm missing something obvious but I can't seem to think of it.
 
Replies continue below

Recommended for you

A residential service derived from one center tapped winding of a wye-delta 3Ø transformer is a single-phase service. All voltages, both legs and the neutral are on the same winding and are electrically in-line. The neutral is halfway between the legs, so the voltage from neutral to one leg is 180 degrees from the voltage from neutral to the other leg.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor