Phase Directional relays Versus Ground Directional Relays

Status
Not open for further replies.

Ooops11

Electrical
Nov 1, 2016
4
Hi there!

Can someone throw some light on this... If 90 Degree connection with RCA 30 OR 45 degrees, can detect and trip on ground fault as well in solidly grounded systems, then why a separate ground fault directional relay is used.

 
Replies continue below

Recommended for you

Hi,

Probably to achieve a more sensitive pickup without
tripping on (forward) load.

Thanks,
Alan
 
Thanks Alan, It makes sense now!
 