Nov 1, 2016 #1 Ooops11 Electrical Joined Nov 1, 2016 Messages 4 Location SA Hi there! Can someone throw some light on this... If 90 Degree connection with RCA 30 OR 45 degrees, can detect and trip on ground fault as well in solidly grounded systems, then why a separate ground fault directional relay is used.
Hi there! Can someone throw some light on this... If 90 Degree connection with RCA 30 OR 45 degrees, can detect and trip on ground fault as well in solidly grounded systems, then why a separate ground fault directional relay is used.
Nov 1, 2016 #2 submonkey Electrical Joined Jan 23, 2009 Messages 71 Location AU Hi, Probably to achieve a more sensitive pickup without tripping on (forward) load. Thanks, Alan Upvote 0 Downvote