HamburgerHelper
Electrical
- Aug 20, 2014
- 1,127
Am I thinking about this correctly? If you have an arrangement with a delta-wye-grounded transformer feeding a plant and a line to ground fault happens on the low side, the phase distance relaying on the high side can overreach to the low side due to load current on the other two phases causing the distance relaying to overreach.
As - phase A secondary - As fault causes fault currents on Aprimary and Bprimary
Bs - phase B secondary - Bs load causes currents on Bprimary and Cprimary
Cs - phase C secondary - Cs load causes currents on Cprimary and Aprimary
Total -
Aprimary + Bprimary (fault current)
Bprimary + Cprimary (Bs load current)
Aprimary + Cprimary (Cs load current)
End result - Aprimary + Bprimary is higher with the load and might cause the phase distance relaying to overreach.