I am having requirements for protection against chnage in phase sequence from the public network, therefore i have phase sequence relays installed in the ATS and in the case of a wrong phase seq on the netowrk, it will work on the generator.
The problem is that people think that the generator is running because there is no public network, so they do not pay attention whereas what should be done is go and see why it started and if it was because of a phase sequence fault then they should contact the local authority as soon as possible since running on gnenerator is much more expensive than running on public network. This is not practical and i do not think they will bother every time. I am thinking of linking this alarm to the set of conditions of a problem in the generator (high coolant temp, low oil pressure, ...) with the only exception that in this case this alarm will be on while the genset is on. This is the cheapest solution.
I am thinking of a more expensive one, a phase sequence corrector. I have my network design for RST sequesnce and i connect the generator accordignly, and i am thinking of the possibilities that can come from the netwrok, they are 6: RST, RTS, SRT, STR, TRS and TSR. So i need 6 phase sequence relays and 6 contactors, with no interlock because logically only one relay can fire at a time. Now i can relax, come what come from the network. Of course it is expensive but i would like to ask if it is viable and if you can point me to something similar?
Thanks.
I am having requirements for protection against chnage in phase sequence from the public network, therefore i have phase sequence relays installed in the ATS and in the case of a wrong phase seq on the netowrk, it will work on the generator.
The problem is that people think that the generator is running because there is no public network, so they do not pay attention whereas what should be done is go and see why it started and if it was because of a phase sequence fault then they should contact the local authority as soon as possible since running on gnenerator is much more expensive than running on public network. This is not practical and i do not think they will bother every time. I am thinking of linking this alarm to the set of conditions of a problem in the generator (high coolant temp, low oil pressure, ...) with the only exception that in this case this alarm will be on while the genset is on. This is the cheapest solution.
I am thinking of a more expensive one, a phase sequence corrector. I have my network design for RST sequesnce and i connect the generator accordignly, and i am thinking of the possibilities that can come from the netwrok, they are 6: RST, RTS, SRT, STR, TRS and TSR. So i need 6 phase sequence relays and 6 contactors, with no interlock because logically only one relay can fire at a time. Now i can relax, come what come from the network. Of course it is expensive but i would like to ask if it is viable and if you can point me to something similar?