Buckeye46
Electrical
- Jun 23, 2018
- 20
Hello,
We had a 69/13.2 delta wye bank fail a few months back and were able to find a new one sitting around somewhere. The issue I am running into is metering. The transformer doesn't have 3 low side CT's nor does it have 3 phase pots on the high side. The design has us using the high side CT's, and a broken delta pot setup on the low side. How could I input this into a satec and still get accurate power factor and etc?? I can easily compensate for the 13.2 to 69 voltage by multiplying by the turns ratio of the transformer but how do I compensate for the 30 degree phase shift??? Is this even possible using a Satec PM174 and no additional equipment?
Thanks.
We had a 69/13.2 delta wye bank fail a few months back and were able to find a new one sitting around somewhere. The issue I am running into is metering. The transformer doesn't have 3 low side CT's nor does it have 3 phase pots on the high side. The design has us using the high side CT's, and a broken delta pot setup on the low side. How could I input this into a satec and still get accurate power factor and etc?? I can easily compensate for the 13.2 to 69 voltage by multiplying by the turns ratio of the transformer but how do I compensate for the 30 degree phase shift??? Is this even possible using a Satec PM174 and no additional equipment?