I would like to obtain valuable inputs to my question and hope I am asking a generic one for my understanding.
A three winding transformer have primary delta, secondary delta and tertiary wye-solidly grounded connected. Primary and secondary winding terminals are connected to separate downstream LV switchboard supplying large rectifier circuits.
The three winding application with this secondary and tertiary winding configuration is expected to create "phase shifting" effects for harmonic mitigation. My understanding and question is as below:
1) I am assuming that the secondary & tertiary phase shifting mitigation effect will only be seen at the primary inputs. The secondary and tertiary harmonic flows from non-linear loads will not be mitigated and hence, the K-factor of the transformer will be calculated based on the total magnitude of secondary and tertiary harmonic flows. Is my assumption correct? The secondary and tertiary are both rated for 480 VAC
2) The total current will be the load plus harmonic currents. Can we actually size the cables to carry both instead of adding expensive Active Harmonic Filters if the primary is within IEEE Std. 519 and the voltage %THD is well within the 1000 V insulation that was specified?
Thank you gentlemen for your opinions and comments.
I would like to obtain valuable inputs to my question and hope I am asking a generic one for my understanding.
A three winding transformer have primary delta, secondary delta and tertiary wye-solidly grounded connected. Primary and secondary winding terminals are connected to separate downstream LV switchboard supplying large rectifier circuits.
The three winding application with this secondary and tertiary winding configuration is expected to create "phase shifting" effects for harmonic mitigation. My understanding and question is as below:
1) I am assuming that the secondary & tertiary phase shifting mitigation effect will only be seen at the primary inputs. The secondary and tertiary harmonic flows from non-linear loads will not be mitigated and hence, the K-factor of the transformer will be calculated based on the total magnitude of secondary and tertiary harmonic flows. Is my assumption correct? The secondary and tertiary are both rated for 480 VAC
2) The total current will be the load plus harmonic currents. Can we actually size the cables to carry both instead of adding expensive Active Harmonic Filters if the primary is within IEEE Std. 519 and the voltage %THD is well within the 1000 V insulation that was specified?
Thank you gentlemen for your opinions and comments.