antxon
Electrical
- Mar 24, 2012
- 4
good morning from Spain.
In my zone the 15-20kv distribution system is grounded by a resistor that limits the earth current to 1000 or 300 amperes depending on the substation (cables or lines).
I'm analyzing an Oscillography of an earth to ground fault. In tis case the transformer has a 13 ohms that limits the 20kv system earth faults to 1000 amperes.
I had the open delta voltage, the high and m.t currents at the transformer and the current that runs through the resistor.
I can't find the relation between the current through the resistor and the open delta or m.t voltages taking in to account the 13 ohms value.
Any clue.
Thanks in advance