Phase To Neutral Calculations

Status
Not open for further replies.

ansible

Industrial
Oct 8, 2008
1
I am planning to run a series of e-ballasts on phase to neutral power, with an equal number of ballasts on each phase for a balanced load. The phase to phase difference is 400v do I use that or the 400/SQRT(3)v when calculating watts. It doesn't seem right that when you calculate watts using

Watts =V*I*pf*SQRT(3)

The answer is greater than the sum of all the ballasts watts. Am I missing something here?

Also am I right in assuming that line and phase voltage can be considered the same if your running the same number of identical ballasts on each phase.
 
Replies continue below

Recommended for you

If the ballasts are connected line to neutral, you need to use the line-to-neutral voltage to compute watts used by each ballast. Then add up how many ballast you have on each phase.

 
Your equation is for a Three Phase Power

3 Phase Watts: SQRT(3)* V(L-L)* I * pf

1 Phase Watt: V x I x pf
 
ansible

dpc and zazmat are correct, in addition, base on zazmat formula.

Basic Ohms Law;

P(Watts) = V x I x pf (eq. 1)

Where;
V = Voltage, per your post, it is 400Volts
I = Current
pf = power factor, assumed as 1

Since you will buy lighting fixtures, the fixtures is complete with lamp and ballasts.

Let us assume 1 Lamp (40 Watts) per fixture. Sometimes, fixture has more than 1 lamp.

To find the line current (I);

From eq. 1;

I (Current) = P(Watts) / V (Voltage) x pf (Power Factor)

Substitute the given data;

I = 40/ 400 x 1

I = 0.1 Ampere

Your last question is confusing. Let me know the following.

1. Does your panelboard a 3-Phase, 4 wire?

2. What is the rated voltage of your input power supply.

If we follow your phase-phase voltage above, it should be 692.8 Volts.

Regards
Bilegan
 
If your phase to phase voltage is 400V then your phase to neutral voltage will be 231V.
1> Select your ballasts for either 400 volts or 230 volts.
2> Use the nameplate watts to determine the energy consumption.
3> Use the nameplate amps to determine the circuit loading and KVA.
4> If you use 400V fixtures you must connect them phase to phase and use a 2 pole breaker.
5> If you use 230V fixtures you must connect them phase to neutral and use a 1 pole breaker.
6> If you connect from phase to neutral you can not use a floating neutral. The neutral must be connected back to the supply transformer neutral.
7> There will be harmonic currents on the neutral and the neutral size must not be reduced.


Bill
--------------------
"Why not the best?"
Jimmy Carter
 
If these are fluorescent ballasts, and you are in canada, they have to comply with he following rule:
(4) Each fluorescent luminaire installed on branch circuits with voltages exceeding 150 volts-to-ground shall be:

(a) Provided with a disconnecting means integral with the luminaire that simultaneously opens all circuit conductors between the branch circuit conductors and the conductors supplying the ballast(s); and

(b) Marked in a conspicuous, legible, and permanent manner adjacent to the disconnecting means, identifying the specific purpose
 
Lefty,
What do they mean by "disconnecting means intergral with the luminaire"? This sounds to me that a switch has to be integrated, that is, a part of, the luminaire. This doesn't sound practical, so I must be interpreting it incorrectly.

K2ofKeyLargo
 
A plug connection will serve.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 