Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Phase to Phase Fault calculation

Status
Not open for further replies.

ChipNJ

Electrical
Joined
May 9, 2005
Messages
2
Location
US
What would the correct formula to use to determine the multiples of a transformers rated OA current and then calculate into actual ampheres?
Transformer:
10 MVA
impedance 8.5%
rated phase to phase voltage (secondary side) 12.47 kV
Supply side capacity 650 MVA
assume impedence angles are the same
assume phase-to-phase voltage at the secondary terminals (prior to the fault) is 12.47kV.
 
I use MVA method for this. Check for the procedure and more the method is capable of doing:

Transformer short circuit MVA :

10MVA / 0.085Zpu = 117.65 SC MVA

650MVA entrance in series with the 117.65 SCMVA is capable of supplying 99.62 SC MVA (X/R assumed to be equal)

Assuming equal 1 and 0 sequence network impedances and X/R ratios, both SCMVA1 and SCMVA2 equal to the 99.62 SCMVA.

The series combination of SCMVA1 and SCMVA2 results in 99.62 / 2 = 49.81 SCMVA.

Ia1 = 49.81 / (1.73 x 12.47) = 2.3kA.

Ia2 = - Ia1 for phase to phase fault.

Assuming B to C fault:

Ib = -Ic = a x a x Ia1 + a x Ia2 + Ia0 =
(-0.5 - j0.866) x Ia1 - (-0.5 + j0.866) x Ia1 + 0 =
-j x 1.73 x Ia1 = 3.98 kA
 
Thanks. I was unsure if I needed to account for the supply side capacity for a fault on the secondary side. Thanks.
 
If you assume that the supply side is an infinite bus, then your answer will always be conservative (i.e. the resulting fault current value will be somewhat larger than if the actual supply impedance is allowed for).

 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top