Phase to Phase rating of cut-outs

Status
Not open for further replies.

Mbrooke

Electrical
Nov 12, 2012
2,546
I semi often encounter distribution substations with paralleled secondaries or large end transformers with low relative Z. The secondary neutrals are always grounded through a 2, 3 or 5 ohm reactor limiting L-G current to 10ka or less. However 3 phase fault currents calculate higher with typical cutouts employed out on the line starting outside the substation. Are ratings higher when considering a phase to phase fault?
 
Replies continue below

Recommended for you

Normally the source impedance will have risen due to line reactance out at the field cutouts, with lower fault currents.
It could be a problem with cutouts close to the sub.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
I see them close to the sub however, first few poles after the riser. It doesn't make any sense to me, but it somehow works?
 
Well.- Sometimes cross arms catch fire. That may be related to your observations. grin