- Jan 5, 2009
- 7
Hello all,
I have a colleague (old school) at work who insists on the use of PICCV for a computer room air conditioner as basis of design. The Lieberts (our preferred vendor) come with either 2- or 3-way valves internal. We prefer 2-way for our datacenter. Either way, my partner insists in taking out the valve that comes with the Lieberts, only to replace them with externally controlled PICCV (Belimo). GPM is about 100 per Liebert. He claims, if we don't do this we would need a circuit setter per Air Handler.... The algorithms for controls (for valve modulation) that Liebert has have worked perfectly in other datacenters I've worked in.
I don't get it... am I missing something obvious?
Thanks!
I have a colleague (old school) at work who insists on the use of PICCV for a computer room air conditioner as basis of design. The Lieberts (our preferred vendor) come with either 2- or 3-way valves internal. We prefer 2-way for our datacenter. Either way, my partner insists in taking out the valve that comes with the Lieberts, only to replace them with externally controlled PICCV (Belimo). GPM is about 100 per Liebert. He claims, if we don't do this we would need a circuit setter per Air Handler.... The algorithms for controls (for valve modulation) that Liebert has have worked perfectly in other datacenters I've worked in.
I don't get it... am I missing something obvious?
Thanks!