I agree with Ron on checking the AS-BUILT. For engineering design, I would tackle the support fixity in following ways:
1.If the column is cast-in-place and the foundation is massive and rotationally restrained (significant section and confined in the subgrade, no matter it is footing block, caisson or pile), the support is closed to “fixed”. Once you have the same reinforcement across the interface, the EI of the interface is the same as the column section. Other than under the seismic loading, unlikely the interface could work in a “yield” state. Even after yielding, the support is not really "pinned" since it continues holding a moment of My. In addition, the section cannot be underreinforced, we usually use in the range of 1 to 3 percent.
2.If the column is precast, the support fixity is dependent on the interface detail. You can make it close to “pinned” or “fixed”. Of course, foundation restraint is another factor.
3.It it always advisable to use “pinned” condition to check the extreme displacement while use “fixed” to catch the most critical internal forces at the interface.