JFMPE
Mechanical
- Sep 22, 2004
- 2
I am designing the pipeline and support system for a 20" diameter hot water (315 psig, 215 deg. F) pipeline. The pipeline will be above ground on 8" diameter pipe piers in 36" diameter drilled holes to various depths. This is a standard design for this type of application in this plant, with thousands of feet of piping on hundreds of drilled pier supports. However previous detailed calculation documents are almost non-existent.
I've been using the Embedded Pole Footing equation for allowable support loading calc's; (non constrained)
d= A/2(1+(1+4.36h/A)^.5), where A=2.34P/S1/b
This is a Seismic Zone 4 area. (Dynamic response loads for the pipeline design have been calculated for these conditions using CAESAR II.)
Hand calculations by others have used a Load Duration Factor of 1.33 for similar designs in the general area. This factor was used to multiply the allowable lateral soil loading, increasing the calculated support loads. How can I verify if this is OK?
[The soils report says for Drilled Pier Foundations;
-Soil Density; 120 pcf
-Allowable vertical bearing @ 5 ft depth; 2000 psf
-Rate increase per foot; 150 psf
-Max. not to exceed @ 20 ft; 4000 psf
-Allowable Positive skin friction per foot; 300 psf/ft
-Allowable Negative skin friction per foot; 200 psf/ft
-Friction angle of soil; 20 deg.
-Undrained shear strength of soil; 1000 psf
-Allowable lateral soil pressure per
foot of depth (UBC formula); 150 psf/ft.
According to the soils report, liquidfaction will not a problem for the project area.]
Thanks for your help.
JFMPE
I've been using the Embedded Pole Footing equation for allowable support loading calc's; (non constrained)
d= A/2(1+(1+4.36h/A)^.5), where A=2.34P/S1/b
This is a Seismic Zone 4 area. (Dynamic response loads for the pipeline design have been calculated for these conditions using CAESAR II.)
Hand calculations by others have used a Load Duration Factor of 1.33 for similar designs in the general area. This factor was used to multiply the allowable lateral soil loading, increasing the calculated support loads. How can I verify if this is OK?
[The soils report says for Drilled Pier Foundations;
-Soil Density; 120 pcf
-Allowable vertical bearing @ 5 ft depth; 2000 psf
-Rate increase per foot; 150 psf
-Max. not to exceed @ 20 ft; 4000 psf
-Allowable Positive skin friction per foot; 300 psf/ft
-Allowable Negative skin friction per foot; 200 psf/ft
-Friction angle of soil; 20 deg.
-Undrained shear strength of soil; 1000 psf
-Allowable lateral soil pressure per
foot of depth (UBC formula); 150 psf/ft.
According to the soils report, liquidfaction will not a problem for the project area.]
Thanks for your help.
JFMPE