I'm trying to size piping to several jacketed tanks (25L, 40L, 60L). Everything will be heated with low pressure steam, and cooled with chilled water.
I calculated the approximate cooling time, and my heat transfer value U appears to be correct based on actual results from a similar tank. I then used the standard m-Cp-deltaT to approximate the cooling load (dividing by cooling time to get kW). To do this, I assumed the heat loss for the water inside the tank was the same as the heat increase in the fluid inside the jacket. I read somewhere that a 5C increase was typical for cooling water, and back-calculated the cooling water flowrate based on this.
If this is all making sense, I am now a little uncertain as to what the pipe size should be. The chilled water flowrate is higher than I expected (6-8 gpm). For a 40L tank, I was assuming it'd be around 3/8 or 1/2 inch NPT. After much searching, even most 3/4 inch lines only average 4-5 gpm, but a larger line seems ridiculous. I think there's an error in my calculations, but I'm not sure what I'm missing.
At the same time, a single control valve will be used for either steam or chilled water. I've seen this work elsewhere, but it also seems a little strange, since steam is so much more efficient at transferring heat?
Is there a resource or guide that explains this? The run from the header is fairly short, so I'm not worried about friction losses. Any help or advice would be appreciated. I can share excel calculations if it helps.
I calculated the approximate cooling time, and my heat transfer value U appears to be correct based on actual results from a similar tank. I then used the standard m-Cp-deltaT to approximate the cooling load (dividing by cooling time to get kW). To do this, I assumed the heat loss for the water inside the tank was the same as the heat increase in the fluid inside the jacket. I read somewhere that a 5C increase was typical for cooling water, and back-calculated the cooling water flowrate based on this.
If this is all making sense, I am now a little uncertain as to what the pipe size should be. The chilled water flowrate is higher than I expected (6-8 gpm). For a 40L tank, I was assuming it'd be around 3/8 or 1/2 inch NPT. After much searching, even most 3/4 inch lines only average 4-5 gpm, but a larger line seems ridiculous. I think there's an error in my calculations, but I'm not sure what I'm missing.
At the same time, a single control valve will be used for either steam or chilled water. I've seen this work elsewhere, but it also seems a little strange, since steam is so much more efficient at transferring heat?
Is there a resource or guide that explains this? The run from the header is fairly short, so I'm not worried about friction losses. Any help or advice would be appreciated. I can share excel calculations if it helps.