Storage occupancy, with the water available I believe I can make it work without a pump.
The downside...I'm looking at 6" main and 4" branchlines. The roof structure is bent metal "z purlins", and the GC has asked for point loads to determine if the steel can support the hangers.
NFPA 13 2010 9.1.1.2 (1) Hangers shall be designed to support five times the weight of water filled pipe plus 250 lb at each point of piping support.
No problem there, using a listed hanger assembly.
9.1.1.2 (2) These points of support shall be adequete to support the system.
Does "the system" refer to the weight of water filled pipe, or do I need to include the safety factor in the dead load as well? If I trapeze the main, and have 2 hangers per length of pipe, hung with sidewinders, I should be well within the purlin limits. Unless I multiply those numbers by 5 and add 250 lbs per hanger. I just want to be sure before I submit any calcs.
Thanks in advance.
The downside...I'm looking at 6" main and 4" branchlines. The roof structure is bent metal "z purlins", and the GC has asked for point loads to determine if the steel can support the hangers.
NFPA 13 2010 9.1.1.2 (1) Hangers shall be designed to support five times the weight of water filled pipe plus 250 lb at each point of piping support.
No problem there, using a listed hanger assembly.
9.1.1.2 (2) These points of support shall be adequete to support the system.
Does "the system" refer to the weight of water filled pipe, or do I need to include the safety factor in the dead load as well? If I trapeze the main, and have 2 hangers per length of pipe, hung with sidewinders, I should be well within the purlin limits. Unless I multiply those numbers by 5 and add 250 lbs per hanger. I just want to be sure before I submit any calcs.
Thanks in advance.