Jun 17, 2015 #1 kayfactor Mechanical Jun 17, 2015 13 0 0 IN Hi All, So as per 8.6.4.1.1.1 (nfpa 13 2013 ed.) the sprinkler can only be 12in from the ceiling. what about in case of structural beams that are running along the roof which are 900mm in depth? Do the sprinklers go 12in below the beam ?
Hi All, So as per 8.6.4.1.1.1 (nfpa 13 2013 ed.) the sprinkler can only be 12in from the ceiling. what about in case of structural beams that are running along the roof which are 900mm in depth? Do the sprinklers go 12in below the beam ?
Jun 17, 2015 #2 TravisMack Mechanical Sep 15, 2003 1,749 0 36 US You will either need to comply with the beam obstructions, or put a sprinkler in every pocket. Travis Mack MFP Design, LLC http://www.mfpdesign.com"Follow" us at https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Upvote 0 Downvote