I hope everyone had a safe holiday weekend.
I have an interesting situation and wonder how some of you would handle it. We are doing a shop drawing based on a complete engineered set of drawings. The plans were done by a PE and approved by the local AHJ. Now, there are many conflicts with the plan and NFPA 13. We have tried to send RFI's for the issues, but the engineer has said that it is not in his scope of work to handle RFI's or construction management issues on the project. I realize these RFI's should have been handled at bid time, but that did not happen.
So, when we have heads that are spaced too far from soffits, sprinklers over spaced for the hazard (160 sq ft in OH1/OH2 areas), improper heads used in concealed spaces (flat concealed space requiring specially listed heads) and several others, how would you proceed?
The AHJ is not much help because he already approved the plans. The PE is not willing to work to correct the errors. Should we fix the plans to install a proper system per NFPA 13 or do we install the engineered plans even though they are incorrect? This would require changing a PE sealed set of contract drawings. I know what we are going to do, but I wanted to get others opinions on this.
This is not meant to be a battle of PE v NICET, as this drawing could just have easily been done by a NICET IV or whatever. In this particular case, it was a NICET IV that did the plans and sealed by the PE. They both work in the same office, so it is not an issue of just paying for a stamp either. It is a question of how you would handle a shop drawing when you have an approved contract drawing that is blatantly conflicting with NFPA 13 in many areas.
Travis Mack
MFP Design, LLC
I have an interesting situation and wonder how some of you would handle it. We are doing a shop drawing based on a complete engineered set of drawings. The plans were done by a PE and approved by the local AHJ. Now, there are many conflicts with the plan and NFPA 13. We have tried to send RFI's for the issues, but the engineer has said that it is not in his scope of work to handle RFI's or construction management issues on the project. I realize these RFI's should have been handled at bid time, but that did not happen.
So, when we have heads that are spaced too far from soffits, sprinklers over spaced for the hazard (160 sq ft in OH1/OH2 areas), improper heads used in concealed spaces (flat concealed space requiring specially listed heads) and several others, how would you proceed?
The AHJ is not much help because he already approved the plans. The PE is not willing to work to correct the errors. Should we fix the plans to install a proper system per NFPA 13 or do we install the engineered plans even though they are incorrect? This would require changing a PE sealed set of contract drawings. I know what we are going to do, but I wanted to get others opinions on this.
This is not meant to be a battle of PE v NICET, as this drawing could just have easily been done by a NICET IV or whatever. In this particular case, it was a NICET IV that did the plans and sealed by the PE. They both work in the same office, so it is not an issue of just paying for a stamp either. It is a question of how you would handle a shop drawing when you have an approved contract drawing that is blatantly conflicting with NFPA 13 in many areas.
Travis Mack
MFP Design, LLC