Dear All,
I am seeking your technical views on API 521 section 5.7.8.8 recommending to have an action of wide plant shutdown at high high liquid level of the flare KO drum specially for upstream O&G facilities with multiple trains where it would be difficult to identify which train is experiencing an emergency while a common flare KO drum is provided among them all for accommodating the relief requirements.
At the same time, API 521 is advising on the time to be considered for liquid emergency release above the point where the plant wide facility shutdown has occured in order to accommodate the continued liquid / gas release, do you agree that the basis of the time provided for the flare KO maximum liquid inventory above the high high level plant wide shutdown emerges from the below underlying consideration:
a- although flare KO pumps are there to pump out the liquid from drum, the drum is considered to be filled prior to the emergency which doesn't consider the reliable power supply to the pumps and hence their unavailability. typically, the level settings below the high level trip setting are set based on normal pump out capacity, so based on the relief rate (even if the drum is initially empty), the time available would be quite too short based on incoming liquid flow rate.
b- upon sensing the high alarm, operator is expected to take action to identify the source of the release and attempt to close the source.
- after surpassing all the alarm setting limits, if liquid build up hits the high high level trip setting and operator failed to close the source, this means the plant is in an uncontroller situation where wide plants shutdown is initiated.
c- The 20-30 minutes nominated by API 521 above the LAHH corresponds to the fact of longer time required to isolate the inlet and identify the source of the release. This also corresponds to the fact that possible the production separator which has experiencing earlier the blocked outlet with liquid build up and release to flare has also failed to close its inlet by the activation of its own SIF function! accordingly, API 521 considers this 20-30 minutes of incoming steady max liquid rate to achieve the maximum level above which sufficient gas cap to be availed to achieve the separation.
d- The gas cap is supposed to consider that as a result of blocked liquid, the gas outlet of the production separator also closed and hence the two phase release has come into the flare KO drum which mandates separation to avoid burning rain/liquid carry over to flare tip.
e- as an alternative to point c, API 521 is nominating the potential implementation of a SIL-3 SIF at the production separator (s) in order to guarantee the closer of the production separator, in this case, API 521 section 5.7.8.8 is nominating only 2-10 minutes time above the LAHH as a liquid release time corresponding to the closing time of the inlet SDVs.
My question is now:
- By shutting down the plan, are we ensure no further cascade effect within the process is happening due to the abnormal situation causing level build up?
- can the 20-30 minutes nominated by API 521 (in absence of a SIL-3 SIF on the production separator) reflects a typical release time of liquid as a result of the blocked in scenario. can this time be demonstrated by dynamic simulations or it would be sufficient to go ahead with the API 521 time basis, is this time historically demonstrated to be good enough for sizing the mutliphase relief into the flare KO drums
- would installing an additional layer of closing an SDV at the inlet of the flare KO drum contribute in reducing the time of liquid release into the vessel.
Thank you very much in advance
Regards,
I am seeking your technical views on API 521 section 5.7.8.8 recommending to have an action of wide plant shutdown at high high liquid level of the flare KO drum specially for upstream O&G facilities with multiple trains where it would be difficult to identify which train is experiencing an emergency while a common flare KO drum is provided among them all for accommodating the relief requirements.
At the same time, API 521 is advising on the time to be considered for liquid emergency release above the point where the plant wide facility shutdown has occured in order to accommodate the continued liquid / gas release, do you agree that the basis of the time provided for the flare KO maximum liquid inventory above the high high level plant wide shutdown emerges from the below underlying consideration:
a- although flare KO pumps are there to pump out the liquid from drum, the drum is considered to be filled prior to the emergency which doesn't consider the reliable power supply to the pumps and hence their unavailability. typically, the level settings below the high level trip setting are set based on normal pump out capacity, so based on the relief rate (even if the drum is initially empty), the time available would be quite too short based on incoming liquid flow rate.
b- upon sensing the high alarm, operator is expected to take action to identify the source of the release and attempt to close the source.
- after surpassing all the alarm setting limits, if liquid build up hits the high high level trip setting and operator failed to close the source, this means the plant is in an uncontroller situation where wide plants shutdown is initiated.
c- The 20-30 minutes nominated by API 521 above the LAHH corresponds to the fact of longer time required to isolate the inlet and identify the source of the release. This also corresponds to the fact that possible the production separator which has experiencing earlier the blocked outlet with liquid build up and release to flare has also failed to close its inlet by the activation of its own SIF function! accordingly, API 521 considers this 20-30 minutes of incoming steady max liquid rate to achieve the maximum level above which sufficient gas cap to be availed to achieve the separation.
d- The gas cap is supposed to consider that as a result of blocked liquid, the gas outlet of the production separator also closed and hence the two phase release has come into the flare KO drum which mandates separation to avoid burning rain/liquid carry over to flare tip.
e- as an alternative to point c, API 521 is nominating the potential implementation of a SIL-3 SIF at the production separator (s) in order to guarantee the closer of the production separator, in this case, API 521 section 5.7.8.8 is nominating only 2-10 minutes time above the LAHH as a liquid release time corresponding to the closing time of the inlet SDVs.
My question is now:
- By shutting down the plan, are we ensure no further cascade effect within the process is happening due to the abnormal situation causing level build up?
- can the 20-30 minutes nominated by API 521 (in absence of a SIL-3 SIF on the production separator) reflects a typical release time of liquid as a result of the blocked in scenario. can this time be demonstrated by dynamic simulations or it would be sufficient to go ahead with the API 521 time basis, is this time historically demonstrated to be good enough for sizing the mutliphase relief into the flare KO drums
- would installing an additional layer of closing an SDV at the inlet of the flare KO drum contribute in reducing the time of liquid release into the vessel.
Thank you very much in advance
Regards,