plastic pipe

Status
Not open for further replies.

johnhan76

Civil/Environmental
May 16, 2002
123
Our client wants to use plastic pipe instead of RCP. The groundwater is within 2' of surface. I am worried about buoyancy forces lifting the pipe up. Does anyone know a quick formula to use to see if it will work or how much cover we need. Thanks
 
Replies continue below

Recommended for you

no quick formula, just sum up the forces
draw your free-body diagram and add up the vectors

downward
weight of pipe
weight of soil over the top

upward
bouyant force

use a safety factor and make sure the resultant is pointing downward
 
ok
safety factor of 1.5 good enough?
 
Just a note....

Don't forget about structures, inlets, catch basins and end sections that will act to secure the pipe. I work in an area with very shallow water tables (Florida) and there is seldom a problem if the structures are not too far apart. Just be careful during construction.