Thanks for the basic data. Now I've got the picture. Your application, from the latest info, seems to be rather benign but I agree with your idea of putting in a rupture disc. Today, I would opt for a buckling pin instead of a rupture disc. This device is much more accurate, cheaper, standardized, and can be replaced with more ease and safety. ProtectoSeal of Bensenville, IL has excellent service and know-how.
Because the fluid involved is water, I'd pipe it with only one elbow pointing downward, and into a potential pool fire.
You are sizing for the Fire Case and trying to "size" your relief during a blocked-in scenario. I still maintain that you have a case where thermal expansion is going to dominate - or your built-in "rupture disc" will activate and relieve -- your gaskets on the plate exchanger! But I would protect the exchanger with the bucking pin anyway - it's the proper, engineered solution. Water has tremendous latent heat requirements - probably one of the highest (if not the highest) in your plant environment. Before it starts to vaporize and generate excessive pressure, it will expand and blow your gaskets (literally!).
I do not believe you will ever generate steam in your plate xchanger before the relief device opens under the Fire Case. Of course, even with the buckling pin open, the unit will generate steam if the fire continues around it. All you need do is install a nominal sized buckling pin such that it's choked flow capacity exceeds the steam generation during the post-relief liquid expansion. The area you use should reflect some factor that compensates for the excess metal exposed. This is not going to be a large device; I would double the calculated area. Don't forget, in these type of scenarios the attempt is to be conservative in estimating the worst case. This is not an exact science, but it can be a safe science. Don't fail to document all your calcs, assumptions, and basic data in your PSM procedure.
I hope this helps.
Art Montemayor