Hello

I am using a Rievtech PLC and a Wecon HMI to log data for a customer I am making an automated test rig for. the issue is that I am trying to use their existing pressure, flow and power transducers that are already powered to obtain an input to the PLC. The Reivetech (PR-18dc-da-r) has a common ground (-ive) connection that clearly these transducers dont share. Infact the input power to the transducers is not the same as the supply to the Rievtech PLC. I am confused how this can be wired up to use the 0-10V output from the transducers in this case. any help would be greatly appreciated.

The other question i have is with the HMD. Its a Wecon 700E. WHat I need is to show the instantaneous performance point on a graph (which is no problem) however I would like this displayed next to the expected performance in pressure and flow. I can not see how I can use a table of data or table or readings to generate a cureve on this HMI. again, any advise on this would be amazing.

Many thanks

David
 
Replies continue below

Recommended for you

To eliminate the common mode voltage between the signal grounds, you need to buy an DC-to-DC voltage isolator for each of the signal channels. The isolators are powered, so the isolator you use must be have 3-way isolation, power supply, isolated from input and output, input and output isolated from each other.

Most isolators are single channel, but there are two channel models available. Here's a link to a variety.

Wire the source voltage signal in parallel to the input of the isolator and then wire the isolator's voltage output signal to the Rievtech PLC AI.

I can't help you with the HMI graph/chart/trend, but I'd search for each of the those terms in the HMI documentation.
 
Hello Dan

That is really helpful thank you. I have an ANU device that i am using to simulate a 0-10 signal for my testing. The ANU has an auto mode that takes an input and then relays the signal. the only issue is it still uses a common ground so I guess what you are suggesting is essentially what I have in the ANU but with comletely different input and outputs.

Thanks for the info... I now konw what to look for :)
 
Yes, an isolator reads the signal on its input side and re-transmits it on its output side, but without any galvanic (electrical) coupling between input, or its power supply. Your problem is not an uncommon problem; there are lots of isolator vendors; lots of choices.

After re-reading your issue with expected performance, I doubt my suggestion will help. Trend and chart are typically terms for display of logged data values over time (Y-t). It appears that you need to find an expected performance value from a temperature vs pressure table.
 
You need a signal Splitter.
Samples:
1.Input:0-5V Power Supply:24V Output:two 4-20mA Type No.: DIN12 IAP- V1-P1-A4
2.Input:0-10V Power Supply:24V Output:0-10V/4-20mA Type No.: DIN12 IAP-V2-P1-V2A4
3.Input:4-20mA Power Supply:24V Output:two 4-20mA Type No.: DIN12 IAP- A4-P1-A4
4.Input:0-10V Power Supply:24V Output:two 0-10V Type No.: DIN12 IAP V2-P1-V2

You could attempt to connect in parallel, although some "Meter Loading" will occur. Connect your DC-Comm to M and tap off the signal to the V1 Input terminal of your PLC.

For trending only HMI that I have seen with X-Y function is "TrendX"
 