New piece of equipment coming soon, total amp draw will be 100 amps. Please check my figures.
100 amp x 1.25 = 125amp x .8 derating the wire = #2 THHN, #8 ground
100 amp x 2.5(inverse timed breaker)= breaker rated 250amps
using NEC 2002 430.52 for breaker calculations.