New piece of equipment coming soon, total amp draw will be 100 amps. Please check my figures.
100 amp x 1.25 = 125amp x .8 derating the wire = #2 THHN, #8 ground
100 amp x 2.5(inverse timed breaker)= breaker rated 250amps

using NEC 2002 430.52 for breaker calculations.
 
Replies continue below

Recommended for you

The breaker x 2.5 is a MAXIMUM size, not a recommended size. If you use that breaker, you must then size the wire for 250A x 125%. Also, I don't know where you got the .8 derating factor on the original wire size you did.

If this is for a dedicated motor branch circuit, the scenario is different by the way.

JRaef.com
"Engineers like to solve problems. If there are no problems handily available, they will create their own problems." Scott Adams
For the best use of Eng-Tips, please click here -> faq731-376
 
D'oh!

Just noticed the reference to 430.52, which means it must be a motor branch circuit. In that case you can use the 250A CB as long as you have an overload relay in your motor controller.

JRaef.com
"Engineers like to solve problems. If there are no problems handily available, they will create their own problems." Scott Adams
For the best use of Eng-Tips, please click here -> faq731-376
 
If this is a single motor then the wire should be OK. You didn't specify a distance. The breaker should never need to be larger than 2X the motor FLA. I would use 150A or 175A.
 