Plotting Overcurrent TCC on High/Low Side of Xfmr

Status
Not open for further replies.

111R

Electrical
May 4, 2012
114
When plotting multiple time-current curves showing coordination between various protection devices, what is typically done to show the coordination between the high and low side of the transformer? If the X-axis shows the multiple of pick-up or current, the low voltage side will be graphed as picking up much quicker than the high side due to the transformer turns ratio. Do I need to reflect the primary fault current to the secondary so the curves reflect the correct coordination?

Thank you
 
Replies continue below

Recommended for you

Yes, you transpose curves using the transformer turns ratio.
 