Thanks for the reply. You said that in this instance, the floor drains should have individual vents, but in my other example thread (With urinals and lavs upstream of floor drains), they didn't? Why do you say this, what is the difference?
The only code evidence for why this floor drain can't be treated as a combination waste and vent (that the floor drain needs an individual vent), is section 915.1 of the 2012 IPC. This states the food grinder waste be on a combination waste / vent system. I assume this would apply to the building drain that the combination waste and vent is connected to, as is the case here.
I interpret the 915.1 of the 2012 IPC saying that combination waste and vent can only serve floor drains, lavs, and drinking fountains to mean that those are the fixtures that don't need an individual vent on them. Any fixture (other than a food grinder), can be located upstream of the combination waste and vent as long as it's properly vented and the building drain waste pipe is oversized. Do you agree?
This is a commercial application, the jurisdiction would follow the 2012 plumbing code.