PMU data in FAC-008

Status
Not open for further replies.

adi 3291

Electrical
Mar 22, 2022
26
Does power system monitoring recorder/PMU data needs to be in the FAC-008 report? If so can you share any evidence regarding the same? Thanks.
 
Replies continue below

Recommended for you

Are you willing to allow it to be damaged by sustained high load current? Would its failure adversely impact your ability to operate the system? It shouldn't impact how the system is protected.

When one this sentence into the German to translate wanted, would one the fact exploit, that the word order and the punctuation already with the German conventions agree.

-- Douglas Hofstadter, Jan 1982
 
Are you asking about data from a PMU? Or evidence about the rating of the PMU recorder itself? Typically FAC-008 reports include verification of the primary ratings of the PTs and CTs, but does not include verification of the secondary side of the instrument transformers.

I assumed all PMU devices probably have 20 amp limits, so they would be aligned with the typical max RF of 4. The might be some ancient metering equipment that has a 10 or 15 amp limit.
 