Hi all, I am looking for explanation of point of fixity of a drilled pier with reference to lateral load capacity design. Any reference to published literature will be highly appreciated. thank you.
 
Replies continue below

Recommended for you

The point of fixity (pof) for a drilled pier will be calculated as you would the point of fixity for a pile. One reference that I have which does a decent job of explaining pof is Pile Foundations by Chellis. It's old, but has good explanations. I would expect that the FHWH manuals will go further into detail. A commonly used software program is L-Pile. It's pretty easy to use, although a bit cumbersome due to the units of input.

As far as picking the exact pof for a pile or pier, that becomes a matter of judgement and some discussions with the structural engineer. I've seen everything used from the second point at which the pile crosses back over the axis of the shaft to the point at which the pile no longer deflects. I'm not sure there is a hard and fast rule for this.

 
The point of fixity will also change with the lateral load.
You can also search for the term "equivalent cantilever length" as this is the same concept.

Davisson has an article that describes a method to estimate the equivalent cantilever length.
Davisson, M.T. and Robinson, K.E. (1965) "Bending and Buckling of Partially Embedded Piles" 6th Int. Conf. on Soil Mech. and Found. Eng..
 