I was asked to design a pole barn and I have always passed on these type of projects because my calcs don't seem to match what the contractor says they want to do and what has worked for them in the past.
The contractor would like to install 4x6 columns 8' o.c. He wants to use a 2x12 beam on each side of the post to support attic trusses.
The building is 30' wide x 48' long. The trusses span the 30'. Trusses spaced 24" o.c.
Ground snow load in my area is 60 psf. Metal roof with 8:12 pitch so the snow load can be reduced to around 33 psf.
When I run the calcs it says a triple 2x12 is needed to span 8' but this contractor and a few other contractors (and online searches) say double 2x12's are fine.
I realize what contractors say and have done in the past does not mean it is correct but I have seen a lot of pole barns built the way the contractor wants to do it and they look great (not structural issues).
Am I missing something? Is there something different about designing a beam for a pole barn.
The contractor would like to install 4x6 columns 8' o.c. He wants to use a 2x12 beam on each side of the post to support attic trusses.
The building is 30' wide x 48' long. The trusses span the 30'. Trusses spaced 24" o.c.
Ground snow load in my area is 60 psf. Metal roof with 8:12 pitch so the snow load can be reduced to around 33 psf.
When I run the calcs it says a triple 2x12 is needed to span 8' but this contractor and a few other contractors (and online searches) say double 2x12's are fine.
I realize what contractors say and have done in the past does not mean it is correct but I have seen a lot of pole barns built the way the contractor wants to do it and they look great (not structural issues).
Am I missing something? Is there something different about designing a beam for a pole barn.