Can anyone help by telling me what the connections are on a poly phase transformer and which connections would be most likely to be used in a factory.

Thanks
 
Replies continue below

Recommended for you

There are typically 6-8 power terminals on the transformer depending on internal configuration. In North America H1, H2, H3 correspond to high voltage phases A, B, C. H0 would be high voltage neutral if applicable. X1, X2, X3 would be low voltage phases A, B, C and X0 the low volyage neutral.

If your adding a transformer a knowledgable person should be involved to ensure phasing of other transformers is the same and transformer configuration is appropriate for your type of system.
 
Generaly Delta/Wye type transformers are used in factories. it has 3 out put point(A,B,C), 1 netural connectin and a grounding connection. first u have to decide power of plant
 