MacMcMacmac
Aerospace
- Sep 8, 2010
- 56
Good Day Folks.
I will not resurrect a thread form 2017 since doing so tends to annoy people, so I will post the URL for the previous discussion and reference the points brought up in the thread.
https://www.eng-tips.com/viewthread.cfm?qid=425800&msclkid=91f8a832cf8a11ec87a484c6f4c25680
In this thread, member Skogsgurra related a novel method employed to soft start 11kv synchronous motors using a 690v feed into a 3300V, 250KVA transformer, using a VFD to slowly bring up the speed on a defibrator at a pulp mill. Full excitation is used from the outset.
I hope Skogsgurra sees this post and can respond to it, but any input is greatly appreciated.
What I would like to know is, are defibrators usually direct coupled to their motors, or were these motors brought up to speed, then coupled to the load. Also, what was the general HP range of these motors. I am assuming these machines are available in a wide range of hp ratings, so I do not suppose anyone else could hazard a guess as to their size.
I am curious about the setup, since we are currently investigating how we can implement a soft start on our 8MW, 13.2KV main synchronous motor which is directly coupled to a 4 rotor, integrally geared centrifugal compressor. We supply exhauster service to our main client with this machine, and they are asking whether there is a way we could provide the flexibility of operation to start and stop this machine several times a day. They are in a cost reduction mindset, and obviously an 8MW exhauster is a large component of the running costs associated with their test campaign. Some of periods of the test would not require the flow provided by the exhauster.
This compressor currently has a DOL starting setup and the currents involved, and the mechanical stresses involved in each start are considerable, which is why we try to limit the machine to one start per day, unless there is a startup fault. If that occurs, there is a timeout to recover the thermal capacity of the motor and another start is attempted. This is not desirable, but we do have contractual commitments to fulfill for our client, so we make an exception in these thankfully rare occurrences. The shorting rings on the rotor have been repaired at least once before for cracks near the holes where the bars go through, so obviously we would like to avoid stressing the motor as much as possible. The machine was built in 1984/85.
Management has investigated the purchase of a VFD and it was about $2,000,000, but I am assuming this is for a full voltage, full power unit. If we could install a low voltage, partial load VFD to accomplish a soft start, it might be far more cost effective. Unfortunately, a compressor coming up to speed will probably present more of a load than a defibrator without material inside it, so it might be not as easy a task to accomplish.
Thank you for any guidance.
I will not resurrect a thread form 2017 since doing so tends to annoy people, so I will post the URL for the previous discussion and reference the points brought up in the thread.
https://www.eng-tips.com/viewthread.cfm?qid=425800&msclkid=91f8a832cf8a11ec87a484c6f4c25680
In this thread, member Skogsgurra related a novel method employed to soft start 11kv synchronous motors using a 690v feed into a 3300V, 250KVA transformer, using a VFD to slowly bring up the speed on a defibrator at a pulp mill. Full excitation is used from the outset.
I hope Skogsgurra sees this post and can respond to it, but any input is greatly appreciated.
What I would like to know is, are defibrators usually direct coupled to their motors, or were these motors brought up to speed, then coupled to the load. Also, what was the general HP range of these motors. I am assuming these machines are available in a wide range of hp ratings, so I do not suppose anyone else could hazard a guess as to their size.
I am curious about the setup, since we are currently investigating how we can implement a soft start on our 8MW, 13.2KV main synchronous motor which is directly coupled to a 4 rotor, integrally geared centrifugal compressor. We supply exhauster service to our main client with this machine, and they are asking whether there is a way we could provide the flexibility of operation to start and stop this machine several times a day. They are in a cost reduction mindset, and obviously an 8MW exhauster is a large component of the running costs associated with their test campaign. Some of periods of the test would not require the flow provided by the exhauster.
This compressor currently has a DOL starting setup and the currents involved, and the mechanical stresses involved in each start are considerable, which is why we try to limit the machine to one start per day, unless there is a startup fault. If that occurs, there is a timeout to recover the thermal capacity of the motor and another start is attempted. This is not desirable, but we do have contractual commitments to fulfill for our client, so we make an exception in these thankfully rare occurrences. The shorting rings on the rotor have been repaired at least once before for cracks near the holes where the bars go through, so obviously we would like to avoid stressing the motor as much as possible. The machine was built in 1984/85.
Management has investigated the purchase of a VFD and it was about $2,000,000, but I am assuming this is for a full voltage, full power unit. If we could install a low voltage, partial load VFD to accomplish a soft start, it might be far more cost effective. Unfortunately, a compressor coming up to speed will probably present more of a load than a defibrator without material inside it, so it might be not as easy a task to accomplish.
Thank you for any guidance.