Hi,
We have a project on-going where we will design-build a containerised portable substation for 11kV vaccuum switchgear. We have built several in the past but not been directly involved in the design.
The feedback from speaking to the project managers involved in these works is that the movement of the portable buildings and the subsequent deflection puts undue stress on the switchgear leading to early failures of bushings etc. An obvious solution is to load the gear in-situ, however this negates the usefulness of a portable sub.
Have enquired with the building manufacturer regarding costs to stiffen the building to keep deflection to 1mm/m (typical of the allowed deflection by many manufacturers), but advised the steel costs will be astronomical.
Another option is to require the busbars, all cables, and bolted connections between panels to be decoupled prior to each move, and reconnected after.
Interested to get some thoughts from similar experiences?
Thanks
We have a project on-going where we will design-build a containerised portable substation for 11kV vaccuum switchgear. We have built several in the past but not been directly involved in the design.
The feedback from speaking to the project managers involved in these works is that the movement of the portable buildings and the subsequent deflection puts undue stress on the switchgear leading to early failures of bushings etc. An obvious solution is to load the gear in-situ, however this negates the usefulness of a portable sub.
Have enquired with the building manufacturer regarding costs to stiffen the building to keep deflection to 1mm/m (typical of the allowed deflection by many manufacturers), but advised the steel costs will be astronomical.
Another option is to require the busbars, all cables, and bolted connections between panels to be decoupled prior to each move, and reconnected after.
Interested to get some thoughts from similar experiences?
Thanks