We have a computer room which is protected by an FM-200 fire suppression system, EPO system and sprinklers. When this building was built in 1996/7 there were no fire extinguishers installed in this computer room.

I have looked though NFPA-1 (2003), OSHA 1910 and local codes but cannot find anything that specifically says a computer room is exempt from portable extinguishers simply because it has protection by a fire suppression system and/or sprinklers.

Does anyone know anything different? We haven't been cited for this by the local or State agencies nor has our insurance inspector said anything.
 
Replies continue below

Recommended for you

Most clean agent control systems include a pre-alarm to allow personnel to control a starting fire, giving you the chance to control the situation without discharging the costly FM200, so fire extinguishers are important. It should be stated in a local code, maybe not indicated as a specific requirement for computer rooms, but a requirement depending of the type of occupancy it is (bussiness, office).

You could also check the NFPA 101 or NFPA 75 to see if it contains clues for your case.
 