Has anyone used bracing similar to what’s shown in the attached image? They call it unsymmetrical portal bracing. I am looking at using this configuration to work around a door. I’m a little uncomfortable having that pinned joint where all of the braces meet under compression and subject to buckling. My thought is to run the primary brace from the base of the column up to the beam above and have the other 2 braces that branch off to the beam-column joints above attached to the primary brace with gusset plates. I typically use more traditional bracing methods so any insight on this or something that might be more efficient would be greatly appreciated. The bay is 10’ wide by 14 ft tall with a 4’x9’ opening at about third span. I originally had a diagonal brace but the door heights were raised from 7’ to 9’ and the brace will no longer clear the door.