bookowski
Structural
- Aug 29, 2010
- 983
I have a condition where we want to install 1/2" adhesive anchors into a slab on metal deck (existing building). The topping slab is 3" thick. All of the Hilti anchors require a minimum overall concrete thickness of 4". The anchor that we are proposing to use has a capacity which appears sufficient for 2.5" embedment. So we could get the required embedment but we don't satisfy the overall concrete thickness that the published values are based on. I spoke to Hilti but they weren't much help and basically said that anything outside of the listed assembly was out of their hands.
We are having pull tests performed on the anchors. Can anyone recommend a source or procedure for test load value and percentage of anchors that could be used to justify or back out a capacity with a certain confidence? Based on nothing other than an initial starting point I was thinking of pulling to 2.0 times ultimate load, so 2 x 1.6 = 3.2 service loads.
We are having pull tests performed on the anchors. Can anyone recommend a source or procedure for test load value and percentage of anchors that could be used to justify or back out a capacity with a certain confidence? Based on nothing other than an initial starting point I was thinking of pulling to 2.0 times ultimate load, so 2 x 1.6 = 3.2 service loads.