dik

Structural
Apr 13, 2001
25,566
0
36
CA
I have a bunch of anchors to spec for a wastewater treatment plant to secure FRP grating and sections to concrete. What is the best material to use? 316 Stainless or a duplex alloy threaded rod epoxied in place?


Dik
 
Replies continue below

Recommended for you

If there are real loads then you need to use real anchors (Hilti or such).
If you are just trying to hold things in place then using epoxy and duplex SS makes sense.
Don't use a threaded rod, the part that is potted should not be threaded. All of the crevices can lead to corrosion issues.
Make sure that water cannot pool at the anchors, assure that the epoxy does not settle and form a pocket.


= = = = = = = = = = = = = = = = = = = =
P.E. Metallurgy
 
Thanks Ed... I was thinking of using Hilti 316 stainless anchors but if a better material was available. Thanks for the heads up on crevice corrosion.