KootK
Structural
- Oct 16, 2001
- 18,395
I could probably find this information in a Hilti manual or by calling a rep but I'm going to start here. I guess I just have a fundamental mistrust of sales literature / people.
Let's say that I've designed a post installed anchor and selected it from a manufacturer's catalogue based on a 30 MPa concrete strength. If the anchors get installed into 20 MPa concrete that hasn't yet reached it's 28 day strength, what does that mean for the anchor capacity in the completed structure? Am I limited to capacities based on 20 MPa? Or will the capacity of the anchors eventually reach that consistent with the 30 MPa assumption? This assumes that the concrete eventually gets there of course.
I'd like comments pertaining to both expansion anchors and drill and epoxy anchors. My intuition is that a drill & epoxy anchor will eventually make it's way to the 30 MPa capacity while an expansion anchor may not.
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.
Let's say that I've designed a post installed anchor and selected it from a manufacturer's catalogue based on a 30 MPa concrete strength. If the anchors get installed into 20 MPa concrete that hasn't yet reached it's 28 day strength, what does that mean for the anchor capacity in the completed structure? Am I limited to capacities based on 20 MPa? Or will the capacity of the anchors eventually reach that consistent with the 30 MPa assumption? This assumes that the concrete eventually gets there of course.
I'd like comments pertaining to both expansion anchors and drill and epoxy anchors. My intuition is that a drill & epoxy anchor will eventually make it's way to the 30 MPa capacity while an expansion anchor may not.
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.