Hi,
I need all of you with in depth knowledge on diesel gensets to help me understand the following statement quoted by two major diesel engine genset manufacturers:
"Diesel engine gensets are rated at 80% PF (example 2000kW/2500kVA @ 80% PF). If the genset load is above 80%, lets say 95%, the genset would consume more fuel. Therefore the recommendation is to disconnect any power factor improvement capacitors when running on genset power".
This is not totally clear for me since:
1.) I am not trying to increase the capacity of the genset, which would clearly result in additional fuel consumption. The load is what it is, with or without capacitors.
2.) Using basic power system principles, any reactive power being supplied from the capacitors downstream from the genset would not need to be supplied by the genset alternator (real power being the same on both cases).
In addition, a typical operating curve for an alternator shows that the alternator could supply loads from almost 0% lagging to 99% leading.
When confronted with my question, one of the manufacturer's responded by saying that the alternator is designed for peak efficiency at 80%, therefore at any other power factor the alternator would not be operating at peak efficiency.
This was not totally true either since the alternator efficiency curve showed efficiency always improved with improved power factor from 0% to almost 100%.
Please shed some light on my analysis of this issue.
I need all of you with in depth knowledge on diesel gensets to help me understand the following statement quoted by two major diesel engine genset manufacturers:
"Diesel engine gensets are rated at 80% PF (example 2000kW/2500kVA @ 80% PF). If the genset load is above 80%, lets say 95%, the genset would consume more fuel. Therefore the recommendation is to disconnect any power factor improvement capacitors when running on genset power".
This is not totally clear for me since:
1.) I am not trying to increase the capacity of the genset, which would clearly result in additional fuel consumption. The load is what it is, with or without capacitors.
2.) Using basic power system principles, any reactive power being supplied from the capacitors downstream from the genset would not need to be supplied by the genset alternator (real power being the same on both cases).
In addition, a typical operating curve for an alternator shows that the alternator could supply loads from almost 0% lagging to 99% leading.
When confronted with my question, one of the manufacturer's responded by saying that the alternator is designed for peak efficiency at 80%, therefore at any other power factor the alternator would not be operating at peak efficiency.
This was not totally true either since the alternator efficiency curve showed efficiency always improved with improved power factor from 0% to almost 100%.
Please shed some light on my analysis of this issue.