edison123
Electrical
- Oct 23, 2002
- 4,462
My client, a steel manufacturer, has an electric arc furnace transformer with power correction capacitors connected on the incoming HV side. During power outage, he has noticed heavy inrush currents and voltage spikes for a very short period. I know that in ac induction motor connected permanently with power factor correction capacitor, heavy inrush currents and high voltages occur during power outage due to induction generator effect created by still rotating motor. Will such phenomenon occur in a transformer-capacitor circuit also ? I reason that transformer being a static unit, there is no stored energy to produce to such transient inrush currents and voltages. Or am I wrong ?