Hi All,
Here are few numbers which I got from a client metering on the secondary side of two 44KV/4160 V transformers T1 and T2.
T1; P= 3 MW
Q= -5 MVAR
S= 6 MVAR
P.F= 52.2 %
T2 P= 2.2 MW
Q= .836 MVAR
S= 2.3 MVA
P.F= -94 %
T1 means, 5 MVAR is the reactive power being absorbed from utility.
T2 means 839 KVAR is being fed back to the utility.
This is a huge mine and full of induction machines and T2 has a 1000 KVAR cap. bank.
I think the meter is not wired properly. I spoke to ION metering tech support and they advised that PF sign -ve means lagging and +ve means leading as per meter conventions.
If I follow the sign conventions that means 5 MVAR is being fed back to utiliy.
How would you guys interpret this meter reading.
Regards