jmbelectrical
Using SKM PowerTools, I was performing a load flow analysis on a project to ensure that voltage drop levels were being kept to a maximum of 3% at panelboards and switchboards. (My state's energy code requires that it be kept to a maximum of 5% at the end load, and our goal is to distribute it such that it is kept at 3% or less to the furthest downstream panelboard,with the remaining 2% occurring along the branch circuit.)
Before going any further, here are a few items that I feel are worth mentioning:
1. The system type is 480/277V, three-phase, four-wire, 60Hz.
2. This is an educational facility, and I was assuming a power factor of 0.9 (lagging) for all loads. Loads generally consist of LED lighting, receptacles, electric space heating, VFD-driven exhaust fans, VFD-driven air handling units, VFD-driven pumps, and air-cooled chillers. Loads were modeled as one "block" connected to each panelboard or switchboard.
3. Feeders with an ampacity of 100A or less are copper with THHN or THWN insulation. Some are in PVC conduit and others are in EMT.
4. Feeders with an ampacity greater than 100A are aluminum with THHN or THWN insulation. Some are in PVC conduit and others are in EMT.
5. I do not have much experience with SKM PowerTools. I typically use a simple, Excel-based, voltage drop calculator.
For most of this exercise, it seemed that the results I was getting were unremarkable. As expected, several, rather long (Anywhere from 200 to 700 feet) feeders with light to moderate loading required increases in conductor sizes in response to excessive voltage drop.
And then I ran into a different situation. A 4,000A switchboard with a demand load of about 2,900A, located about 150 feet from the utility transformer, had a voltage drop of around 3.5%. Its service feeders were comprised of 12 sets of 600kcmil aluminum conductors with THWN insulation. Increasing the conductors' size to 750kcmil helped, but the voltage drop still exceeded 3%. Changing the conductor type to copper brought it down to almost exactly 3%, but this was problematic since the voltage drop exceeded 3% at the downstream panelboards. The utility transformer can only accept a maximum of 12 sets of conductors, with a maximum conductor size of 750kcmil. I had hit a roadblock.
Upon bringing this to my boss's attention, he recommended adjusting the power factor of the load to unity, citing similar experiences on other projects. Doing so brought the voltage drop down to under 1.5%. Using the Excel-based voltage drop calculator referenced above yielded similar results. It seems that it assumes a similar power factor.
This leads me to the following questions:
1. I've never taken power factor into account when performing voltage drop calculations in the past. I know that the effective impedance of a conductor changes depending upon the power factor of the load, and I know that the voltage drop due to a conductor's reactance becomes more of an issue when dealing with larger conductors. In your opinion, when should power factor be taken into account?
2. Was my original, assumed power factor of 0.9 reasonable or was it too conservative for a facility of this type?
3. Is assuming a power factor of unity the right thing to do in this scenario?
4. Does SKM PowerTools have any "quirks" that may have skewed the results? Is there a possibility that I modeled something incorrectly?
Thanks to all for any input provided.