Please help:
A 3-phase induction motor rated 150hp(110kw) has a constant running load of 104 Amps per phase at approximately 466 volts across phases.Norminal pf is about 0.87
We noticed about 10Amps drop per phase when the pf was corrected upwards to about 0.95 using third party equipment.
How best can I translate this drop of (10A)to KWh over a 24hr period to try and estimate the savings, here is what I have:
KW = V(phase)*I(phase) * sqrt(3)*pf where v=466, i=10, pf=0.95
Kwh=kw*24
Will this work?