Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

Power Supply Calculations 1

Status
Not open for further replies.

Camomac

Electrical
Oct 12, 2011
4
0
0
AU
Hi,

If you have a Power supply, that supplies a load of 15Amps at 13.8VDC, how would you calculate the current on the AC side of the supply (@240V). (this information could help with circuit breaker sizing etc?)

If you have to assume an efficiency for the power supply and a input power factor, lets say 90% efficiency and 0.95 pf.

Thankyou
 
Replies continue below

Recommended for you

OK, so apply conservation of energy. Don't forget to include a power factor correction, though...

TTFN
faq731-376
7ofakss
 
Hi,

15Amps at 13.8VDC = 207W

90% efficiency....power on AC side = 230W

P = V*I*pf
230 = 240*I*0.95

I = 1.009A???

Would this we the correct answer?

Sorry Macgyver, this was a discussion I was having with a friend and thought we would get a confirmation.

Thankyou for your responses
 
Hello all,

@Camomac, you got it right in the calculation. However, it holds good only for a 1-Ph system as the input. For a 3-Ph system, dont forget to add "Root 3" to the formula.

Fahad Shaikh
 
Status
Not open for further replies.
Back
Top