rickei

Electrical
May 27, 2009
6
Hi there,
I have to design three phase transformer for power supply: 13000VDC @ 10ADC, cap filtered.
Using capacitor filter always makes me nervous because of figuring transformer's secondary voltage and current.
Is it OK if I calculate Us=0.74*UDC , Is=0.816*Idc , and because of cap filter increase transformer's kVA about 50% ?
Thanks,
 
Replies continue below

Recommended for you

Realistic. Yes.

But if you need voltage to stay well regulated as load changes, you may need to do better. What are your specs?

It is a rather big unit. It may pay to contact a specialist company.

Gunnar Englund
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
 