Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Power to a drive. 2

Status
Not open for further replies.

sech

Electrical
May 4, 2007
2
I have a customer that is hooking up a drive that requires 332V. The voltage supplied to the plant is 480V. The transformer that I have found is a 480V-380Y/220. Is there anyway to apply an external tap or other device to make the voltage get with in the 332V requirements?
 
Replies continue below

Recommended for you

Hi,

Is this a servo drive? They sometimes have special input voltage specificatrions.

An autotransformer is usually used to adapt voltage. And that is usually also mentioned in the manuals for the drive.

Gunnar Englund
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
 
Is it the drive that requires 332V, or is it the motor.
With many inverter drive systems, it is possible to specify the output voltage at a given frequency and this is independent of the input voltage provided that it is less than or equal to the input voltage. - no transformer required if this is the case.

Best regards,

Mark Empson
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor