Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Power Transformer LV Coordination - Inrush

Status
Not open for further replies.

BuggyBrent

Electrical
Jan 17, 2006
2
I have a 10 MVA, 69/13.2 kV transformer. It has HS and LS fuses. My question is how concerned should I be that the LS fuse coordinates with the transformers inrush curve? Do the LS devices actually see the curve or is it seen only from the HS devices? I have not found a definitive answer through various text books.
 
Replies continue below

Recommended for you

The inrush is a business strictly between HS side and line. You can have funny voltages on the low side during the inrush. But nothing that the LS fuses care about.

Gunnar Englund
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
 
The coordination is only for through fault currents.
The Transformer energisation inrush is felt only by the fuses on the source side of the transformer.
 
In most cases, the transformer will not be energized from the low-side.

I thank everyone for their posts.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor