Dear Folks,
In our project specifications, I have seen the sizing calculations of transformer and is calculated by:
(continuous load X 1 + Intermittent Load X 0.3 + Stand-by Load X 0.1) X factor of safety(1.2)
Anyone pl. explain how to calculate factors for intermittent loads and stand-by loads and if any standards (IEC / IEEE) available, pl. let me know.
Advanced thanks...